Buck Boost Transformer
Little Bill
Tennessee NEC:2017
Semi-Retired Electrician
If you fed a 240V/120V 24V/12V BB transformer with 208V, what would the boost voltage be?
The transformer was mounted on the side of an air compressor but neither the air compressor or transformer were hooked up.
Depends on how you wire the transformer. The split primary will presumably be wired with both coils in series, since 208V > 120V.
If you wire the split secondary with both coils in series (nominal 12V configuration), then the turns ratio will be 240V:12V = 20:1. So with 208V on the primary, the secondary will be 208V/20 = 10.4V. Wired in a boost configuration, the boosted voltage will be 208V + 10.4V = 218.4V.
If you wire the split secondary with both coils in parallel (nominal 24V configuration), then the turns ratio will be 240V:24V = 10:1. So with 208V on the primary, the secondary will be 208V/10 = 20.8V. Wired in a boost configuration, the boosted voltage will be 208V + 20.8V = 228.8V.
Cheers, Wayne
Cheers, Wayne
Thanks, I knew it was close to 230V but didn't know how to figure it.
Oops, I swapped the series/parallel descriptions for the two possible secondary configurations.
Hopefully I elaborated the steps of the computation sufficiently for you to be able to duplicate it in the future.
Cheers, Wayne
Cheers, Wayne
You mean the 12V configuration should have said parallel, and the 24V configuration should have been series?