Dedicated circuits and modern appliances
clemver
PA
I've been doing a lot of kitchen remodels lately and wondering what everyones feelings are on something.
Most recent one was a very decent remodel. Aside from the standard appliances they had (2) ice makers, (2) wine coolers, and (2) trash compactors. Now per the manufacturer under their electrical specs all it says is "requires dedicated 15A supply circuit". OK, added subpanel it is.
Once the appliances arrive, stickers on them show ratings of like 1.2A. I get that we have to install per manufacturer instructions, but c'mon. With lengthy homeruns, cost of AFCI/GFI combos, and breaker spaces being prime real estate in these houses, I think it's silly.
Now I know a bus full of nuns isn't gonna burst into flames if I combine even SOME of them. But I also know god forbid something happens to their $3000 ice maker and manufacturer finds out it ISN'T dedicated, I'd be more upset than I was buying those 6 extra breakers. Guess I'm just ranting. That is all.
Rant is well deserved. Manufacturers are horrible at applying code the their products. Technically the NEC does not use the term dedicated supply circuit so it has no real code meaning. If it said individual branch circuit then that is in the NEC.
Yea can't remember what the exact wording was but, point still stands. I'm not so much worried about code, other than 110.3(B), or failing inspections moreso like I said voiding any warranties because it was hooked up "wrong". BIG quotations around that.
I had a similar situation but the ice maker I had to wire was 100 watts. It called for a separate circuit. I didn't install a new circuit. Btw, I believe the reason that the manufacturer calls for a separate circuit is because they don't want any interference on the circuit which may cause an issue with their product.
Absolutely about the reasoning. I'm also imagining something else on the circuit causing a trip, fridge goes out, homeowners livid that the "fridge is busted" and takes it out on manufacturer. Dedicated eliminates that at least that.
Unless the mfg sends a tech out for a problem, how would they ever even know the item wasn't on a dedicated circuit? I even doubt a tech would know when he came to check it.
Or if he would bother. I have never seen one check and they are usually a contractor who is getting paid to get it working not finding out how to weasel out of getting it fixed.
I would like to offer (without hope of anyone agreeing) the opinion that if this "spec item" was not explicitly included in the product's listing, then we are not required (by the applicable code article) to comply.
Have fun, y'all!
I would counter that one circuit can be dedicated to more than one load, especially multiple similar small loads.
Have fun, y'all!
I would argue that dedicated could just mean "other than general". As in, "That 20 amp circuit is dedicated to those two mini fridges and that ice machine "
I agree with this Larry, but you missed my point. We must follow the instructions that are part of the product's listing. I submit that a manufacturer putting a requirement in an installation or operation manual does not mean that they included this requirement when they subjected the product to whatever tests and inspections it underwent in order to get it listed.
Charlie, I'm not talking about any differences between testing and instructions. I'm saying that a single "dedicated" circuit supplying more than one appliance is in compliance with those instructions.
Now if these appliances are in a kitchen that would be a violation of SABC being 20A of 210.52(B)(1) unless using exception 2 then it must be on its own circuit.
A guess is the mfg in effort to "cheapen" the appliance are listing the appliance as only 15A