brother
Senior Member
I remember there was a time when we didn't need to support emt with short runs of 24 inches. Then the code changed and took that away, What was the reason behind that? nec 358.30 (A) and (B)
The reason is stupidity on the part of the CMP. There was one code cycle the 2008 {250.30(C)} where short, unbroken sections of EMT (18" or less) did not require support. The next code cycle that was removed. If that isn't stupid I don't know what it.Then the code changed and took that away, What was the reason behind that?
I would argue a piece of emt less than 36” between two boxes is securely fastened in place. The boxes are required to be rigidly secured to the surface , the emt fitting/connectors on both ends secure the conduit to both boxes,The reason is stupidity on the part of the CMP. There was one code cycle the 2008 {250.30(C)} where short, unbroken sections of EMT (18" or less) did not require support. The next code cycle that was removed. If that isn't stupid I don't know what it.
Wowl. lol I guess we will have to try to correct the stupidity. As far as Im concerned if they can allow a conduit to be supported at 3ft, (5ft in some instances) then why can we not have an unbroken ( no coupling) emt between to boxes with the same rule?The reason is stupidity on the part of the CMP. There was one code cycle the 2008 {250.30(C)} where short, unbroken sections of EMT (18" or less) did not require support. The next code cycle that was removed. If that isn't stupid I don't know what it.
Well in terms of exception 1 I think he was right and it was not applicable, you were running parallel with the framing members so you have every opportunity to use the stud to secure the emt , 358.30 (a)exception 1 is intended to apply to conduit ran perpendicular to ceiling framing members , if the roof supports spanned 5’ and yiu put a box on one rafters you wouldn’t have to drop a support within 3’ you could secure the conduit at the structural member 5’ from the box as long as it was a unbroken length of conduitWowl. lol I guess we will have to try to correct the stupidity. As far as Im concerned if they can allow a conduit to be supported at 3ft, (5ft in some instances) then why can we not have an unbroken ( no coupling) emt between to boxes with the same rule?
Reason this came up I had a situation where we had a 'technical' debate at work about a short run of emt between 2 boxes and its a warehouse type no finished wall just studs. So the vertical run is just under 24 inches, box to box. open stud, I was of the interpretation that a support was not needed because of the exception NEC 2023 358.30 No.1 .......When structural members do not readily permit fasting within 3ft.
Heavy emphasis on the 'readily permit'. LOL. He says readily permit is not defined, but readily accessible is. he claims the studs can permit install a support.
I view 'readily' is being almost existing and not needing cross bars or wood or other installs to put a support. lo.
I read PI 2359 as well as both yours and Mr Holts Pc’s regarding this and I would’ve thought your pc would be accepted based on committee statement resolving PI 2359 when they said up to 3’ is already allowed , but the pc proposed the language to clear up any confusionIt was removed because of PI from the IAEI that said the rule in the 2008 code required additional supports and the CMP agreed. The PI for the 2008 rule called for a 36" length and the CMP accepted in part by changing the 36" to 18".
There have been a number of attempts to fix this issue for EMT, IMC, and RMC. They all had the same rule in the 2008 code.
Most inspectors ignore the actual code language and permit a straight, unbroken, 36" length to be supported by the conduit terminations.
Who is P ??It was removed because of PI from the IAEI that said the rule in the 2008 code required additional supports and the CMP agreed. The PI for the 2008 rule called for a 36" length and the CMP accepted in part by changing the 36" to 18".
There have been a number of attempts to fix this issue for EMT, IMC, and RMC. They all had the same rule in the 2008 code.
Most inspectors ignore the actual code language and permit a straight, unbroken, 36" length to be supported by the conduit terminations.
PI- public inputWho is P ??
They may have or have not intended it that way, but that is not what it says. ;-) One can say the same as about the ceiling, they could have ran it parallel instead of perpendicular, it would look weird but it can be done. lol ;-) So there goes my interpretation.Well in terms of exception 1 I think he was right and it was not applicable, you were running parallel with the framing members so you have every opportunity to use the stud to secure the emt , 358.30 (a)exception 1 is intended to apply to conduit ran perpendicular to ceiling framing members , if the roof supports spanned 5’ and yiu put a box on one rafters you wouldn’t have to drop a support within 3’ you could secure the conduit at the structural member 5’ from the box as long as it was a unbroken length of conduit
That being said i like I mentioned in my prior comment I feel that 2’ piece of emt you had between two boxes satisfied 358.30(A) and was securely fastened in place
While I will say the language used in the exception may not be completely clear as to intent, but the explanatory material from the nfpa link enhanced content speaks to intent , and I’ve always read it the same wayThey may have or have not intended it that way, but that is not what it says. ;-) One can say the same as about the ceiling, they could have ran it parallel instead of perpendicular, it would look weird but it can be done. lol ;-) So there goes my interpretation.
I agree with you, the 3ft, or my honest opinion the 5ft should be OK with 2 terminations of boxes.
What was their justification?IAEI submitted a Public input stating the rule in 2008 required additional supports, and it passed , the cmp accepted what they proposed
I honestly don’t know , Don is the one who mentioned the IAEI PI that was proposed and accepted , brother asked Don who P was I was just explaining it was a PI @don_resqcapt19 how did the Cmp justify acceptING the proposal from the IAEI ?What was their justification?
-Hal
But the result is you need a strap for a 2" length now.The justification was that the change that said you don't need a strap for 18" of pipe meant that you needed to have one and that would make an inspector's job more difficult. I'm going off of memory and using my own words, but it was something as crazy as I am making it sound.