Hi.
How can I design the neutral conductor for a PV inverter according to NEC 2023?
The inverter is a SMA Core 1, 62.5 kW-US. The manufacturer indicates that this inverter has less than 3% of THD.
The phase conductors are going to be 1/0 AWG (because of voltage drop)
Several colleagues indicate that balanced systems do not need the neutral, at all. Others than non lineal systems must be sized 100% of the phase conductors and a few told me to size the neutral as the EGC per 250.122.
This should be ok for 1 inverter, but in my case, I must install 40 Core 1 in a single project. This means 40 x 100%-sized conductors represent a big part of the budget.
I just need the correct Code reference to justify this to the inspector.
Thanks in advance.