Hello folks,
I had a question regarding the verbiage of section 310.15(C)(1) in conjunction with the verbiage of 366.23(A).
310.15(C)(1) states conductors not maintaining spacing for a continuous length longer than 24 inches requires an adjustment factor. Since 366.23(A) references the code section, and not just the table itself, would a gutter box with more than 30 current carrying conductors in a cross-section, need to be for a continuous length of more than 24 inches in the gutter box, in order to require adjustment factors?
I ran into the gutter box below, with more than 30 current carrying conductors in cross section however, it is only for a length of about 16 inches.
		
		
	
	
		
	
Sent from my iPhone using Tapatalk
	
		
			
		
		
	
				
			I had a question regarding the verbiage of section 310.15(C)(1) in conjunction with the verbiage of 366.23(A).
310.15(C)(1) states conductors not maintaining spacing for a continuous length longer than 24 inches requires an adjustment factor. Since 366.23(A) references the code section, and not just the table itself, would a gutter box with more than 30 current carrying conductors in a cross-section, need to be for a continuous length of more than 24 inches in the gutter box, in order to require adjustment factors?