Rules for installing low voltage reactors
Tainted
New York
Engineer (PE)
What are the rules that govern installing low voltage reactors (less than 600V) for limiting fault current?
All I could find is NEC article 470 sections 470.1, 470.2, 470.3, 470.4 and that's it...?
must it these reactors be treated like in article 450? Are there any other rules outside of the NEC for installing the low voltage reactors?
I don't think there are any special rules for installing reactors. They are just equipment.
Reactors are not transformers so nothing in article 450 should apply.
Can't you put the reactors on the MV side?
Just need to put a reactor to lower fault current. But I think I'll pass due to high voltage drop and long lengths still being required
.... high voltage drop and long lengths still being required
This is why LV reactors are not commonly seen in the real world as solutions to high fault currents.
At least a transformer usually comes with taps to overcome the voltage drop.
I think you are not allow to use tap to overcome the voltage drop.
It will cause overvoltage when load is low.
Yes that is a consideration. It depends on how much voltage drop is caused by the transformer versus a simple reactor.