We've received a correction from the AHJ stating that a 10" x 10" x 96" horizontal wireway installed below three panelboards (each being 24"wide x 9" deep) is a pull box and must be increased to 20" in height due to the fact that we have installed 2.5" conduits under-slab and up into the wireway. We then have 2.5"diameter x 3"long nipples connecting the wireway to the panelboards.
AHJ is saying that this is a pull box and that per NEC 314, the 2.5" conduit size x 8 for a straight pull through a pull box brings us to a "pull box" height of 20".
I believe this to be a wireway because the conductor pulling concludes once in the wireway and the conductors are then formed and fed up and through the conduit nipples into the panelboard.
What do you say?
My apologies, I've got a photo but apparently I'm not yet allowed to attach photos because I just joined.
What do you say?