Can I pretty please get a clear definition of what "storable" means in 680, because I'm not sure my common definition is what the code considers "storable", or maybe it is...
If it's a prepackaged unit that you lay on a patio, is that storable or merely "self-contained" (also where is "self-contained" referenced in 680?)?
Also:

If it's a prepackaged unit that you lay on a patio, is that storable or merely "self-contained" (also where is "self-contained" referenced in 680?)?
Also:
- does the part IV disconnect need to be toggle/lever style, or can it be a pull-out air condition sort?
680.41 "A clearly labeled emergency shutoff or control switch...." - finding a sub to trench. Who am I looking for, landscapers? How much of a PITA is it to trench 60ft on your own (power tool assisted)?
- Install instructions state to use #6 wire. It's a 40A circuit, with #8 already being <2% Vdrop. I guess I must do this as it's instructions?