I have a question.
I was working at a Fairgrounds that has 100 kva, Single phase padmoumt transformers that feed 200 amp 120/240 vac Load Centers mounted to Utility poles.
I found that the neutral and ground is bonded at the Padmount and they also had the neutral and ground bonded at the Load center with a grounding electrode(ground rod).
In my view this is a safety hazard, because of the parallel path back to the source.
I feel the neutral and ground should be separated at the Load center.