ptonsparky
Tom
- EC - retired
Insulation is not perfect. It leaks current. It's the reason GFCI protection at the source end of long DB conductor will trip.What is leakage current?
You know people say that some stuff is a conductor and other stuff is an insulator? That's not really true. Everything is a conductor, but some conductors really suck. We use the worst conductors as insulation.What is leakage current?
That kind of leakage is generally due to capacitance, assuming the voltage is below the insulation rating. Is still real current though and enough of it will trip GFCI devices.Leakage current is pretty much any current that flows in an undesired path (leakage) in a normally functioning system. This would include the tiny current through a completely intact insulation system.
so it sounds like leakage current is a commonly misunderstood concept. I’m assuming it’s intended to mean “current that physically penetrates the insulation of conductors” ( likely unintentionally). Or as someone else put it, insulation conducts electricity, just very poorly.That kind of leakage is generally due to capacitance, assuming the voltage is below the insulation rating. Is still real current though and enough of it will trip GFCI devices.
And that leakage current would typically be traveling from conductors to metal parts / egc yes?Insulation does actually conduct, and not just capacitively. It may just be nano- or picoamps, but over a long enough distance it can be substantial.
Yes and to other conductors. The insulation is like a resistor between the conductors. A really really high value resistor.And that leakage current would typically be traveling from conductors to metal parts / egc yes?
Everything is a conductor if a high enough voltage is applied![]()
Which brings up the point regarding the first response, in that if ANY parts of either systems are referenced to ground, that ground connection completes a circuit.If you think about it, what is described in the first post is exactly what we do when we 'ground' a system. The 'neutral' is just one of the system terminals, and its voltage is not defined until we connect it to 'everything else' by grounding that terminal. You could equally ground any of the terminals (though some won't be permitted by code; the physics would allow it).
You can read any value between two non-referenced points. In your case 277V L-G is most likely in a balanced system, like one with no load, however the real world is not always balanced. It is even possible to read up to 2X L-L during some fault condition.What potential would you read line to neutral point in an ungrounded wye (you can have an ungrounded 277/480Y I believe). You would still get near nominal voltages yeah? In my mind the grounding of your transformer would not substantially not effect the available fault current value.