Elsewhere in the world, 30mA is considered safe for protecting personnel, it's just that it is above the "let go" threshold (but below the cardiac arrest threshold). So they will not be able to let go until it trips, but it will not stop their heart. (Probably).
I have looked into why this is, such as RCD protected public swimming pools in Europe.
RCD's are more
time sensitive than UL 943 devices down to 30ma, I modeled the standards IEC 61008 to UL 943 at various currents to test UL 943 Class A compliance above 30ma (not not a GFPE breaker but a actual IEC 61008 RCD) UL 943 defines class A as allowed to trip in T = (20/I)^1.43 seconds
At 45ma (150% of 30ma for a ground fault) a UL 943 device must trip by .313 seconds or 314 milliseconds (ms)
30ma RCD breaker (RCBO) trips in 300ms = pass.
Drop it down to the 30ma threshold of the RCD UL 943 goes up to 560ms;
RCD trips in 300ms = pass
At 60ma (2x) UL 943 is 207ms. RCD tripping time is 150 ms = Pass.
And so on.
The only thing that a RCD does not pass UL 943 is (of course) is below 30ma UL 943 will allow a trip time of 1 second (1000ms) at 20ma.
A 5ma ground UL 943 trip time is 7260ms or about 435 cycles of 60Hz.
as we know most industrial installs have good equipment grounding a so 5-29 ma ground fault potential can be mitigated by a EGC.
In Europe and Asia they have about every possible type of 230V (220 - 240V) you can imagine (grounded, ungrounded, delta, wye ... etc) so a RCD is also good on any 240 60 hz system we have like hi-delta where a UL 943 is not for over 150V to ground.