woodduder
 - West Central FL.
I am looking for some feedback for wire sizing for DC cables that run from battery storage cabinets to a 300KVA UPS.  I have been in this business for 40 years, but 99.99% has been involved with 120/208 and 277/480 volt AC systems.
I now have a UPS system with a separate battery storage cabinet, that I must connect with cables. I just need some reassurance that I am thinking correctly since this is not AC wiring.
The battery cabinet has a maximum voltage of 575VDC and a max current of 511 amps. My thoughts are to install 2 individual 2" conduits between the battery storage and the UPS. Each conduit to have two (one red, one black) 300 KCMIL conductors. 300KCMIL THHN good for 285 amps at 75 degrees = an ampacity of 570 amps. Seems good so far. Let me know if I am wrong so far.
Next issue. The wiring space is tight. I have been told I should be using "welding cable" as it would bend better in the tight space. I have never used "welding cable". I received a quote for OMNI CABLE B225001 (this is 250 KCMIL). What is the ampacity of this cable? I cannot find this info. Cable has an EPDM insulation, but this is not in NEC. I am going to call OMNI, but any input would be great.