Property inspector here- central VT without code enforcement to set the stage.
I have a meter that has a 4 wire SER feeding the main service panel, which is located about 25-30 feet away. The SER runs from the exterior meter directly inside and through the crawl space and up to the meter located in a closet. My understanding is that his should be a 3 wire SEU and then a bond of the neutrals and ground should occur inside the service panel or a disconnect needs to be installed behind the meter. Also the grounds and neutrals are bonded and terminate on the same bus bar inside the service panel. Am I wrong? An electrician here says I am. Please excuse any wrong terminology. Thank you.
I have a meter that has a 4 wire SER feeding the main service panel, which is located about 25-30 feet away. The SER runs from the exterior meter directly inside and through the crawl space and up to the meter located in a closet. My understanding is that his should be a 3 wire SEU and then a bond of the neutrals and ground should occur inside the service panel or a disconnect needs to be installed behind the meter. Also the grounds and neutrals are bonded and terminate on the same bus bar inside the service panel. Am I wrong? An electrician here says I am. Please excuse any wrong terminology. Thank you.