Alwayslearningelec
- NJ
- Estimator
When you do a vd calc and you have either 120/208 or 277/480 how do you know which voltage to input. e.g. 277/480 which would it be?
The load electrical data tells me that?What ever voltage the circuit operates at.
Yes. For the case of a 208Y/120 system (the larger number goes first for 3 phase systems), you could have a 2-wire 120V circuit, a 2-wire 208V circuit, a 3-wire 120/208 circuit (this one's a bit tricky, you'd ideally look inside the equipment connected and consider it as a combination of the previous two cases), a 3-wire 208V 3-phase circuit (3 phase voltage drop has a different factor in the formula compared to 2-wire single phase voltage drop), or a 4-wire 208Y/120 circuit (again, you'd ideally look at the loads supplied and consider it as a combination of the other cases).The load electrical data tells me that?
Each state has its own energy code and thats where the code requirements for voltage drop are found.When you do a vd calc and you have either 120/208 or 277/480 how do you know which voltage to input. e.g. 277/480 which would it be?