SQD NF Panelboards breakers w/Aux contacts
PanelGuy1315
Louisville
Electrical Designer
Hello All,
I have a question about the SqD NF style panelboards. We require the breakers that come with the Aux contact built-in but they take up a 4th pole on the board. This means when we install multiple of these breakers next to each other, the phasing will be different. First breaker will be A-B-C, but the second will be B-C-A. Is this common to do?
My electrician is trying to space the breakers apart so that each one is A-B-C, but this is wasting some breaker space that we had reserved for future loads.
This panelboard is feeding control panels with DC power supplies and field mounted VFDs.
There is no requirement to have A phase be the top pole on a 3 phase breaker. You have the same issue where there is a mix of 2 and 3 pole breakers, or even a mix of 1, 2, or 3 pole breakers.
You typically fill the spaces in order...unless you are installing single pole breakers in a high leg panel.
I think the thought is that maintenance could be confused by phasing being inconsistent across multiple breakers. I don't think the loads will care.
The sequencing of the phases wouldn't change A->B->C->
Thanks for this reply. That makes sense. I hadn't thought about a mix.