We have a system where three (3) 2000kVA gensets are paralleled onto a common switchgear. When we run our fault calculations in SKM we assumed all generators are running at the time of a fault. Therefore at the time of a fault, as a rotating machine, each generator will contribute fault to the system for a short period of time like a motor would. We submitted our report as such showing the three (3) generator mounted breakers (NOT on the paralleling gear) failing because the combined fault current from all three gensets is greater than the AIC of the breakers (100k). The gear itself is fine as it is rated 200kA.
Here is where we disagree with the EOR on their response back. They are trying to direct us to run the fault calculations for the generator breakers as if the fault itself is isolating one generator from the system. They're claiming that the genset breakers will only see contribution from the OTHER two gensets at the time of a fault.
I disagree because if there is a fault when all three gens are running, all three will contribute fault current to that device. I understand that if there is a fault at one of these breakers it will isolate one generator from the rest of the system, but it will still contribute fault current to the main CB in question. Therefore, the fault current MAY be to high for the breaker to actually isolate the fault as intended.
Does this make sense? Am I a moron?
Here is where we disagree with the EOR on their response back. They are trying to direct us to run the fault calculations for the generator breakers as if the fault itself is isolating one generator from the system. They're claiming that the genset breakers will only see contribution from the OTHER two gensets at the time of a fault.
I disagree because if there is a fault when all three gens are running, all three will contribute fault current to that device. I understand that if there is a fault at one of these breakers it will isolate one generator from the rest of the system, but it will still contribute fault current to the main CB in question. Therefore, the fault current MAY be to high for the breaker to actually isolate the fault as intended.
Does this make sense? Am I a moron?