Why can't you? Are you thinking of something specific?how come you can’t protect a 21 amp rated conductor with a 20a ocpd for brach circuits
You can always protect a larger conductor with a smaller breaker. The breaker/OCPD just has to be equivalent, or less, to the conductor.Everything i’ve read states this.it was strange to me
This is not the case, so you either stated something incorrectly, or are misunderstanding the issue.how come you can’t protect a 21 amp rated conductor with a 20a ocpd for brach circuits
Im not talking about limiting the protection to 20a and talking about the conductor protection based on the conductors rating limitations…… good nightThis is not the case, so you either stated something incorrectly, or are misunderstanding the issue.
If you have a LOAD that is rated to draw 21A, you cannot use a 20A rated conductors for that, and since the OCPD is protecting the conductors, putting a 20A OCPD would be indirectly wrong as well.