In the nec a 500kcmil rated at 380 can be protected with a 400a ocpd ( next size up) how come you can’t protect a 21 amp rated conductor with a 20a ocpd for brach circuits
 
Everything i’ve read states this.it was strange to me
You can always protect a larger conductor with a smaller breaker. The breaker/OCPD just has to be equivalent, or less, to the conductor.

You might have to adjust the EGC due to the ungrounded conductors being increased in some cases.
 
how come you can’t protect a 21 amp rated conductor with a 20a ocpd for brach circuits
This is not the case, so you either stated something incorrectly, or are misunderstanding the issue.
If you have a LOAD that is rated to draw 21A, you cannot use a 20A rated conductors for that, and since the OCPD is protecting the conductors, putting a 20A OCPD would be indirectly wrong as well.
 
This is not the case, so you either stated something incorrectly, or are misunderstanding the issue.
If you have a LOAD that is rated to draw 21A, you cannot use a 20A rated conductors for that, and since the OCPD is protecting the conductors, putting a 20A OCPD would be indirectly wrong as well.
Im not talking about limiting the protection to 20a and talking about the conductor protection based on the conductors rating limitations…… good night
 