Yeah thats usually my go to I suppose I'll stick with that.I would take the 36 amp min circuit and divide by 125%.... 28.8 amps
That's clearly non-conservative, as the MCA is from a formula of the form: MCA = 125% * A + B + C + D etc. Dividing the whole thing by 125% would give you A + 80%*B + 80%*C + 80%*D etc. Whereas we want, as a minimum, A + B + C + D.I would take the 36 amp min circuit and divide by 125%.... 28.8 amps
Valid point thanks but article 220 can't expect disassembly of the 'MCA' for a load calc, when a Run Load Amps (RLA) and or Full Load Amps (FLA) are provided? Is that not the meaning of those terms?That's clearly non-conservative, as the MCA is
That very well could be, but that would be a huge issue for Trane and whatever listing agency listed the product to correct. I emailed their tech support and ask that they confirm the FLA and RLA numbers and they did.I think the Trane data is in error.
They all do that, in proportion to RLA. Most usually end up with MOCP of around 2 to 2.5 times the RLA, but MCA is still only 125% of RLA plus other loads.MCA & MOP numbers but he did not know but speculated its because LRA is 48A and it will pull that at startup then drop down to 14.7.
You must have gotten a poorly informed technical support worker. A little more research shows that the Trane XV19 line of units are inverter driven. I'm unclear on the rules for nameplate labeling on inverter driven HVAC units. But the product line spec sheet at https://trane.com/WEBCACHE/22-1940-1D-EN_10122021.PDF shows that the line includes 2, 3, 4, and 5 ton units. The correspond nameplate data are:Not saying Trane is correct but I took steps to notify their tech support, explaind its for a service load calculation and they confirmed the numbers and confirmed that's what they intend the published RLA and FLA are for, load calcs.
The only conservative choice for "nameplate rating" for this unit is MCA.
Article 220 only requires 100% load, that is by my understanding RLA and FLA, I don't see anything in article 220 would mandate using an MCA in a article 220 load calculation other than for a branch circuit,I think the Trane data is in error. Their product data publication 22-1940-1C-EN dated 31 Mar 2020 uses 12.4 for the RLA for 3 ton, 4 ton, and 5 ton units. It would be highly unusual for 3 ton, 4 ton, and 5 ton units to have the same compressor RLA. There is a note in the electrical table in publication 22-1940-1C-EN that says in part for the compressor RLA, "The value shown is the branch circuit selection current."
A 12.4 RLA for a 5 ton unit doesn't pass the smell test. I don't think the laws of physics have changed, and no matter how many operating steps a variable speed unit has I don't think you can get 5 tons of cooling with a compressor motor that's about 2 HP based on the RLA. Trane's 4TTV8X series is 12.4 compressor RLA for 3 ton, 16.0 RLA for 4 ton, and 19.3 for 5 ton. The 5 ton 4TTV8X has an MCA of 27.0. The compressor in a Daikin DZ17VSA601B is 29.0 RLA.
I don't trust Trane's numbers. To stay on the conservative side I would use ((36.1 - 2.3) X 0.80) = 27.0 for the compressor RLA and 29.3 amps as the running load for the unit.
You must have gotten a poorly informed technical support worker.
OK, but the data available to you clearly indicates that RLA + FLA is not 100% of the load.Article 220 only requires 100% load
To expand on that (my edit time expired):OK, but the data available to you clearly indicates that RLA + FLA is not 100% of the load.
To me its clear thats point of putting the Full Load Amps (FLA), HP, and Run Load Amps (RLA) for fan motors and compressor motors on a nameplate for a Article 220 calculation. I could see it being a trick question on a exam, 'whats the minimum calculated load when the nameplate says...'To expand on that (my edit time expired):
I guess since 220.82 refers to the "the nameplate rating(s) of the heat pump" it is reasonable to say that the plural option is there to allow you to add the RLA and FLA and any other individual loads listed, rather than just using the MCA.
UL 60335-2-40 requires it to be marked correctly and describes how to do it including a variable speed drive compressor but I am no expert on refrigerant compressor motors. Perhaps its like my '20HP shop vac' the UL sticker says it draws 5A at 120V, or a 2HP garbage disposal that only draws 4 amps... marketing fluff?You have enough data available to conclude the nameplate is wrong.
Certainly for Article 220 Part III. For 220.82 it's not quite as clear.To me its clear thats point of putting the Full Load Amps (FLA), HP, and Run Load Amps (RLA) for fan motors and compressor motors on a nameplate for a Article 220 calculation.
Great, but now you are presented with a nameplate where it is pretty clear it is not marked correctly. So you need to determine how to proceed with your calculation in this unusual case. I strongly advise against using "12.4 + 2.3", that is significantly non-conservative.UL 60335-2-40 requires it to be marked correctly
The name plate matches the data sheet you found on their website so if the nameplate was incorrect I'd expect a mismatch, also the manufacture said the numbers are correct.Great, but now you are presented with a nameplate where it is pretty clear it is not marked correctly.
I was also using 228.83, my understanding from UL 1995 (which is admittedly out of date) is FLA and RLA are the appropriate numbers used in calculations.Certainly for Article 220 Part III. For 220.82 it's not quite as clear.
36.3 The equipment shall be plainly marked, in a permanent manner, with the following:
the horsepower (see Clause 36.18) and full load amperes of each motor, except for hermetically
sealed compressor motors, which shall be rated in locked rotor and rated load amperes (see Clause
36.10), and motors smaller than 1/8 horsepower, which may be rated in watts or amperes;
g) heater input amperes or watts at marked voltage. See also Clause 36.3(t) for separable heater
element assemblies;
If the nameplate is wrong on something I dont think you'd go ahead and accept it and try to guess what the correct value is? You'd reject the equipment as who knows what else is defective and its a expensive unit.So you need to determine how to proceed with your calculation in this unusual case.
Not necessarily, that would be obvious to anyone who cross checks. But if both the spec sheet and the nameplate are wrong (e.g. the numbers on the spec sheet were developed during the design, but with typos, and then production takes those numbers to make the nameplate), that's not quite as obvious.The name plate matches the data sheet you found on their website so if the nameplate was incorrect I'd expect a mismatch
On the face of it, the pattern of RLA data in that spec sheet is not consistent with physics. Also, the pattern of RLA and FLA data is not consistent with the pattern of the MCA data., also the manufacture said the numbers are correct.
https://www.trane.com/WEBCACHE/22-1940-1D-EN_10122021.PDF
Well, if the nameplate only had RLA and FLA on it, I agree you'd be stuck. But it also has MCA and MOCP, which do follow a plausible pattern. And for branch circuit sizing, those are the important numbers, so the ones that likely got a bit more attention paid to them. So given that, it is reasonable to still trust those numbers (or at least trust them more than the RLA).If the nameplate is wrong on something I dont think you'd go ahead and accept it and try to guess what the correct value is?
I don't think a typo on a nameplate impugns the entire product, likely nothing else is wrong with and it works fine.You'd reject the equipment as who knows what else is defective and its a expensive unit.
It wont pass inspection and would be a serious UL violation, plus I dont know what numbers are correct perhaps the MCA and MOP are wrong then?I don't think a typo on a nameplate impugns the entire product,
I agreeOn the face of it, the pattern of RLA data in that spec sheet is not consistent with physics.