Correct. To be considerate of the future not-so-thorough person working on the circuit, you could label the 50A spa disconnect as being supplied by a 30A feeder, but it's not required.I just wanted to make sure it didn't matter if the spa disconnect was 50 amp but the over current is 30 amp.
Possibly can be a little more useful to add such label if the spa panel has open spaces and someone might be considering adding more circuit(s) to it.Correct. To be considerate of the future not-so-thorough person working on the circuit, you could label the 50A spa disconnect as being supplied by a 30A feeder, but it's not required.
Cheers, Wayne
I propose a new section in Article 110. Installers shall be considerate of future servicing by using labels that explain the installation.Correct. To be considerate of the future not-so-thorough person working on the circuit, you could label the 50A spa disconnect as being supplied by a 30A feeder, but it's not required.
Cheers, Wayne
Why do you have two accounts?Not a bad idea
To yell at himselfWhy do you have two accounts?
There are spa's that can run on 120 volt 20 amp circuit or on 50 amp 120/240 volt circuit. The difference is changing a setting on the main control board. The pump always runs on 120 volts. But takes up enough circuit capacity when on high jets mode there is no more capacity for other loads to run. When in the 120 volt mode, the pump runs on low speed and the heater draws only 25% or what it does when connected to 240 volts - this can all run on 20 amp @ 120 volt circuit. If you put it in 120/240 mode the heater has four times the capacity and can heat while using the spa as well on a 50 amp circuit.It actually does require two circuits, I ran a separate 20 amp 120 volt circuit for the pump that will be on a GFI receptacle and the pump will be switched from an air switch. The 30 amp 240 volt circuit is for the heater. Do you see any issues?