I've been about everywhere else with no luck. Around 2 weeks ago my wife called and said that the newly installed in-ground pool was "zapping them". I check voltage and read 1.8-2 volts with the power prod in the water and ground on the deck. Checked by the house under the meter - grounded to the wire on the ground rods and red probe in the dirt, getting 1.8. Checked one neighbor an out 100 yards away, they have 1.8 at their meter on the ground, while the other neighbor shows 4.6. Had two new ground d rods installed today, no change. If the bonding wire is removed from the pool pump, voltage drops to almost nothing in the pool. We've killed every breaker while watching the water voltage - pool sub panel, main panel, and every single breaker in the house - voltage remains. I did install a ceiling fan on the back patio recently - any chance that's the culprit before I take it down to check? Would that affect the neighbors? From what I'm reading as response to others, I need to get EMC involved. We've had a good bit of weather and storms lately and this seems to be a rather sudden thing. Also, on the same day the pool shocked them, my doorbell transformer went out and the garage door went nuts for a few hours. House built Sept of 2023. Help me, smart people.