But the motor is subject to the ambient temperature of the area that is being exhausted, correct? That ambient will increase with reduced airflow.I follow what you are saying, but the motor is not in the airflow path. The fan is belt driven.
Generally, restricting the airflow lowers the fan HP.Has anybody checked for air flow restriction? This will cause the motor to overheat and fail. Also just adding a bigger motor in such case will not fix it, but only exacerbate the issue. A duct system is designed for a specific flow and a restriction of any sort will increase the resistance to the motor rotation, and subsequent heating. Two considerations, was the motor when replaced at some point sized to the design specs. of the ventilation system, and is there some other restriction happening, fan bearings failing, over tensioning of the belt drive etc.
Maybe not. The fan and motor are on the roof. If less air is being exhausted, the ambient temperature could be lower.But the motor is subject to the ambient temperature of the area that is being exhausted, correct? That ambient will increase with reduced airflow.
They are axial fans. The latest one is a downdraft. The others are updraft. Doesn't change what the real problem is. Where they are is hotter than they are rated for.I don't remember if this an axial flow or centrifugal. Details keep trickling in that change everything.
Similar to calling Dr. and saying 'my foot hurts, what's wrong?' ...click
Look at "Farm Duty" single phase motors, they are usually Class F insulation.For single phase motors, I have only seen Class B. Custom made motors? Not gonna happen for this customer. Am thinking the best path is to mess with the pulley sizes and strive for 80% of FLA.
Explosion proof Farm Duty might be a trick to find.Look at "Farm Duty" single phase motors, they are usually Class F insulation.
He now states that the motor is roof-mounted and not in the flow of air being exhausted from the building. I wonder why it’s XP?Explosion proof Farm Duty might be a trick to find.
I know.He now states that the motor is roof-mounted and not in the flow of air being exhausted from the building. I wonder why it’s XP?
He said they were axial., mounted on the roof.He now states that the motor is roof-mounted and not in the flow of air being exhausted from the building. I wonder why it’s XP?
Fan is axial, belt driven.He said they were axial., mounted on the roof.
Oops, I missed that.Fan is axial, belt driven.
Because it is a natural gas compressor building. The fan is to ventilate any released gas in addition to heat from the internal combustion engines driving the compressor. The better designed compressor building will shutdown if there is not enough fans running.He now states that the motor is roof-mounted and not in the flow of air being exhausted from the building. I wonder why it’s XP?
OP described a fan similar to that as what he has, but with a 40C motor driving it. Thinking he wants explosion proof as they must be considering the area near the fan outlet to be a classified location as it could be exhausting natural gas at times?In case you or the customer gets tired of replacing explosion proof motors, or searching for, higher temperature non existent 1Φ ones, they may consider a fan replacement that is suited for the purpose.
These are commonly used for paint booth's, paint curing ovens and paint mix room exhausts. The motor is totally isolated from the airway and located outdoors on the roof mounted models. The belt drive is also isolated in it's own enclosure, sealed off from the airway. They can be had with a base that sits on a roof curb, and have a blow open cap on the top of the stack. The discharge stack can be added to extend the discharge height, above the roof if required
The motor and belt drive sheave can be enclosed in it's own rain proof enclosure with a service door. The motor can then be a standard NEMA model with whatever insulation class rating you desire, but standard TEFC ones last for many years when located outdoors on the roof in it's rain proof doghouse. And as far as temperature is concerned they are rated up to 200 F in the airway. Can be had from several manufacturers. A couple examples.
NYB Tubeaxial Fans are designed for moderate-pressure ventilation & industrial-process use where axial flow is desirable & space is at a premium. Contact us today!www.nyb.com
Ah. I missed that it was XP…Explosion proof Farm Duty might be a trick to find.