Exhaust Fan Motor "Burning Up."
Hey! I could have them bring in 3-ph service and install a VFD driven fan, with class F insulation, to keep the existing single-phase, with class B insulation, exhaust fan cool! (Sarcasm)
You’re close! Replace the existing fan motor with a 3 phase motor with class F (or H) insulation powered by a VFD fed from the existing single phase. This was alluded to in post 4.
For the sake of argument, a 3hp 3-phase explosion proof motor can be had for under $1000. From my poking around a 2 hp single phase explosion proof motor is north of $2k. Depending on where you can install stuff (size of classified area), it may not be that much more to put in a motor with F class insulation and run it on a VFD. Something to consider.
If the classification is D2, an explosion-proof three phase motor wouldn’t be required.
OP described a fan similar to that as what he has, but with a 40C motor driving it. Thinking he wants explosion proof as they must be considering the area near the fan outlet to be a classified location as it could be exhausting natural gas at times?
That's the reason I suggested a sealed Tubeaxial style fan. If the discharge stack is extended upwards away from the drive, it removes the drive from the hazardous discharge zone. Combine that with an spark resistant aluminum blade and that gives you a unit suitable for conveying and discharging flammable gasses and vapors with approved means. Suitable for elevated temperatures as a plus. It also can be provided with a Standard 1Φ or 3Φ motor as desired.
It's been the standard in painting and baking systems for almost a century. Very low maintenance other than belt adjustments and replacements