I have a 4 unit town house that I used 220.84 to calculate the load for the entire building. The stove that is to be used is 15KW at 240V. This is the sum of all 4 burners, oven element, and broiler element.
Am I allowed to use 220.55 to get by using a maximum demand of 8kW+((15kW-12kW) * 5%) = 8.15kW?
It just doesn't make sense to me to use 15kW for the calculation as no one is going to have all elements running full steam.
Or is it assumed the 45% demand factor I can apply from 220.84 accounts for this?
Thanks