Just a retired commercial electrician but here is my 2¢. The  numerous 100 HP 4 Pole plain Jane NEMA frame 480 volt motors that I installed & PM'ed had 124 amps FLA  So a 100, 150'& 200 HP 480 Volt three phase motors would have a combined ampere of 558 amps if my old brain is correct. That is too high of a current for a 600 amp circuit breaker. If all three motors were on VFD'S with at least a 20 second ramp up time and maximum Hertz reduced somewhat ( if your system  can deal with reduced running speed  ) you should be able to get away with it until a larger circuit breaker along with larger wire are installed.