We have a 480V SWGR that gets input from 2-500kVA Emerg generators when there is an outage.
There is no ATS and the two generators feeders terminate in 1600A CB. There is also a MCB that gets its supply from a normal 480V source.
They want to manually close 1600A CB when there’s a outage (which doesn’t lineup with Nec 700 or 701).
In addition there is no kirk-key interlock between the MCB and the feeder CB.
There seems to be multiple code issues here
Enviado desde mi iPhone utilizando Tapatalk
There is no ATS and the two generators feeders terminate in 1600A CB. There is also a MCB that gets its supply from a normal 480V source.
They want to manually close 1600A CB when there’s a outage (which doesn’t lineup with Nec 700 or 701).
In addition there is no kirk-key interlock between the MCB and the feeder CB.
There seems to be multiple code issues here