Hello,

I have done service upgrades before but with the code changes and PG&E changes of how they are processing service upgrades, I would like to know if this install would be ok. Would love to know other alternatives or suggestions. Others have brought up using a switch gear but I think it might be overkill for this application.


 
What he said. ^ Seen one one like this recently with two meter mains. Should be okay. You should NOT need fused discos.

Until manufacturers update the meter packs to have separate compartments for each breaker, the trough may be the only fully compliant way to do 2-6 meters like this.
 
Thanks for the confirmations. Also, would you guys bond the neutral and ground at the trough or at all the meter mains? Would the grounding electrode conductor enter from the trough or meter main?
 
Thanks for the confirmations. Also, would you guys bond the neutral and ground at the trough or at all the meter mains? Would the grounding electrode conductor enter from the trough or meter main?

MBJ is still installed at the first point of disconnect, regardless of what comes before.

Essentially it’s no different than the N-G bond in single meter main, and a metal riser and weatherhead.
 
Thanks for the confirmations. Also, would you guys bond the neutral and ground at the trough or at all the meter mains?

Trough can be bonded to the neutral. MBJs still required in all meter mains; meter mains are factory bonded anyways.

Would the grounding electrode conductor enter from the trough or meter main?
NEC allows either the trough or GEC taps to each meter main. I don't think PG&E has a problem with taking the GEC to the trough, but your local AHJ might call it inaccessible and make you do taps to the meter mains.
 