430.102(B) Motor.
A disconnecting means shall be provided for a motor in accordance with
430.102(B)(1) or (B)(2).
(1) Separate Motor Disconnect.
A disconnecting means for the motor shall be located in sight from the motor location and the driven machinery location.
(2) Motor Controller Disconnect.
The motor controller disconnecting means required in accordance with
430.102(A) shall be permitted to serve as the disconnecting means for the motor if it is in sight from the motor location and the driven machinery location.
Exception to (1) and (2):
The disconnecting means for the motor shall not be required under either of the following conditions if the motor controller disconnecting means required in
430.102(A) is lockable in accordance with
110.25:
(1)Where such a location of the disconnecting means for the motor is impracticable or introduces additional or increased hazards to persons or property
Informational Note No. 1:
Some examples of increased or additional hazards include, but are not limited to, motors rated in excess of 100 hp, multimotor equipment, submersible motors, motors associated with adjustable-speed drives, and motors located in hazardous (classified) locations.
(2)In industrial installations, with written safety procedures, where conditions of maintenance and supervision ensure that only qualified persons service the equipment