We are pulling wire in existing conduits( one 2" and another 2" spare). The distance is 700'. 500' is underground pvc and 200' is interior overhead 200' RMC.
We are running from an 277/480v 800A breaker in a distribution board to 277/480v 800A panel HH-01-1-EXT-DPH-E-1. They want us to size the wire.
A few questions regarding voltage drop calc I'm using.
1. I'm inputting 480v and not 277 for the panels. Is that correct?
2. Should I really put 800A for current at end of run? I can safely use 80% of that?
3. As I said above they ran one 2" and one 2" spare. Even if I use 640A(80% 800A) I need both sets of 2" and would have ot run 600 MCM.
THoughts? Thanks