Hello All,
110.26(A) states that 3ft working clearance is required for equipment likely to require examination, adjustment, servicing, or maintenance while energized. Well, ESS (Energy Storage System) is 'set it and forget it' installation and no examination, adjustment, servicing, or maintenance while energized in the field. If there's anything wrong with it, the ESS is likely sent back to the manufacturer. So my question is: Can 12 inch deep ESS installed on a wall of a 3ft wide exterior walkway? This walkway is on a side of a residential house.
Thank you.
110.26(A) states that 3ft working clearance is required for equipment likely to require examination, adjustment, servicing, or maintenance while energized. Well, ESS (Energy Storage System) is 'set it and forget it' installation and no examination, adjustment, servicing, or maintenance while energized in the field. If there's anything wrong with it, the ESS is likely sent back to the manufacturer. So my question is: Can 12 inch deep ESS installed on a wall of a 3ft wide exterior walkway? This walkway is on a side of a residential house.
Thank you.