Section (A) applies only to dwelling units, section (B) applies only to other than dwelling units, section (D) applies to both dwelling and non-dwelling. The unamended NEC requires GFCI protection for all ranges everywhere, including hardwired.
If you have any way not to enforce GFCI protection on ranges, it is wise to do so. Many common ranges nuisance trip the GFCIs so much that people can't use their range at all. I have spent several years digging into it and it is not a problem that is fixable by the electrician. I don't expect it to get better for another 3 years at least.
There are extensive threads on this subject on this forum (
https://forums.mikeholt.com/threads/range-tripping-gfci-210-8-555-53.2582546/), and I have collected a whole bunch of white papers and reports and expert opinions on the subject that I would be willing to send you if you DM me. That provision has been amended out of several state codes and we amend it out locally as well.