P Pinnie Senior Member Location Ohio Occupation Commercial Electrician Jul 6, 2025 #1 Subtext under the picture says ungrounded systems in hospitals are typically single phase two wire. Is that true? Grok disagrees.
Subtext under the picture says ungrounded systems in hospitals are typically single phase two wire. Is that true? Grok disagrees.
roger Moderator Staff member Location Fl Occupation Retired Electrician Jul 6, 2025 #2 Don't trust Grok, it's true see 517.160
P Pinnie Senior Member Location Ohio Occupation Commercial Electrician Jul 6, 2025 #3 roger said: Don't trust Grok, it's true see 517.160 Click to expand... That’s why I came here thank you
roger said: Don't trust Grok, it's true see 517.160 Click to expand... That’s why I came here thank you
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jul 6, 2025 #4 While single phase two wire is the most common hospital isolated systems, there are 3-phase systems and 517.160(A)(5) provides the required colors to be used for the identification of the conductors of a 3 phase isolated ground system.
While single phase two wire is the most common hospital isolated systems, there are 3-phase systems and 517.160(A)(5) provides the required colors to be used for the identification of the conductors of a 3 phase isolated ground system.