Dsg319
Senior Member
- Location
- West Virginia
- Occupation
- Wv Master “lectrician”
How do these circuits even work? Cross neutrals somewhere out in the house?
Standard 40ckt service panel (pre emergency disconnect era)
Sometime along the line someone added an additional neutral bar and from what I can tell there is NO bonding screw nor a wire type bonding jumper so is no way physically attached to the service neutral in the panel. But obviously I still read continuity and circuits still work off this neutral bar.
I come across this while just adding a 50amp gfci breaker for a camper.
My question is how do these circuits even work? Just in series through the loads throughout the house that have the neutral that are on the original bonded neutral bar.
And possibly mis matched crossed neutrals somewhere in device box or j box?
Either way I’m going to install a wire typer bonding jumper back to the original neutral bar that is bonded to the panel.
Standard 40ckt service panel (pre emergency disconnect era)
Sometime along the line someone added an additional neutral bar and from what I can tell there is NO bonding screw nor a wire type bonding jumper so is no way physically attached to the service neutral in the panel. But obviously I still read continuity and circuits still work off this neutral bar.
I come across this while just adding a 50amp gfci breaker for a camper.
My question is how do these circuits even work? Just in series through the loads throughout the house that have the neutral that are on the original bonded neutral bar.
And possibly mis matched crossed neutrals somewhere in device box or j box?
Either way I’m going to install a wire typer bonding jumper back to the original neutral bar that is bonded to the panel.