kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
You mentioned earlier it is Iline. I-line is notn obsolete although certain breaker types that fit I line panels have been discontinued but there most likely is something else available that will work in place of the type you have. Basically need to know voltage and AIC rating needed to determine what will work. 480 or 600 volt breakers will work on 208 or 240, but 208 or 240 volt breakers can not be used on 480 or 600 volts. They all plug onto any I-line bus.Seems the breaker might obsolete. But as others have mentioned there other compliant solutions.
How long is the run to the disconnect? It possibly can still be compliant if it fits conditions of any feeder tap rules and you do have proper overcurrent device at the disconnect. More than 25 feet and inside the building, forget it you need proper protection on supply end.