Somebody is probably misinterpreting something here. There is no “3 legs of 277V”. That is a 480V system and for some reason, they are using 3 separate power supplies with each one connected phase to neutral. That might be inside of the unit, but that’s not the same as a 3 phase power supply.
Be that as it may, you cannot be guaranteed that a 480V system in this country will be 480Y277. MOST new systems will be, simply because utilities like simplicity and consistency from a maintenance and spare parts standpoint. But anyone can ask for an exception to have a 480V delta source and get the exception granted if they have sufficient cause. In addition, it USED TO BE quite common for heavy industry. 480V delta was/is used when the cost of an inadvertent shutdown due to a minor ground fault would cause far more economic chaos than that of the lost equipment. So in an ungrounded delta system, the first ground fault simply changes it to a corner grounded delta, and the rest of the plant keeps on chugging along unaware. This concept was VERY common in plants built during WWII, especially if it involved “strategic materials” such as steel, aluminum, mining, textiles, petroleum products and chemicals. The practice continued for a long time afterward and still happens today, just not as often.
I cut my teeth in this industry as an electrician at a steel mill, we were 480V delta. We had “phase lights” in the electric shop and if one of them glowed brighter than the others, that told us there was a ground fault somewhere on that phase. We didn’t know where, so we would all jump into golf carts and spread out across the campus looking for either a column of smoke, or a production manager running around pulling his hair out because his line was down and he wasn’t going to make quota!
In addition, a LOT of sites that only use 480V machinery will have a 4 wire TRANSFORMER from the utility, because that’s the default, and the XO terminal is bonded at the transformer or the service panel. But they don’t bother running a neutral conductor out past that point because the are not using it. This is VERY common in Motor Control Centers, because motors never need the neutral. So if your equipment ends up at a place like that, it’s not going to work. Someone needs to rethink this design IMHO…