If you don’t mind my asking what do these motors do?I have 48 120v motors to hook up. These motors draw 2.6A with 5.1A at startup. Being these motors are all plugged into 20a receptacles can I still upsize the OCPD for startup current or do I need to stay at 20A OPCD because of the receptacle?
They are up in a ceiling for air filtration motors so they will not be accessible from the floorSee Table 210.21 (B)(3) Since it's a receptacle you have to stay within the listing. What would keep someone from unplugging the motor and using the receptacle for some other equipment?
Then you run into not being able to have receptacles above a ceiling.They are up in a ceiling for air filtration motors
not above the ceiling. Located on the ceilingThen you run into not being able to have receptacles above a ceiling.
-Hal
What says you can't have receptacles above a ceiling?Then you run into not being able to have receptacles above a ceiling.
-Hal
As long as you don't have anything plugged into them permanently.What says you can't have receptacles above a ceiling?
Years ago we were told one of the biggest issues with receptacles installed above drop ceiling was cords used most likely would produce toxic fumes during a fire. One funny inspector said he only allowed receptacles above drop ceilings wss for cell.phone chargers. Was a continuous fight with the people who made the connections for overhead projectors. I always installed a dup!ex receptacle in the drop ceiling facing down so power cord was not in an drop ceiling that was used for air return. ( air plenum ) . Never found out if any company manufacturers a little 1/10 HP or so sump pump with an approved cord & 120 volt male plug that is listed for inside of drop ceilings. One company had a dozen of them for HVAC units that they removed and cleaned several times a year.What says you can't have receptacles above a ceiling?