hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have cord and plug connected appliance that draws 13A. The engineer has specified 20A receptacle but the plug rating is 15A. Should not the plug be 20A as well?
An appliance with a 15 amp plug is permitted on either a 15 or 20 amp circuit. That's why 20 amp receptacles have a T slot for either configuration.
The manufacturer of the equipment determines the size of the plug based on the listing. 1800 watt hair dryers have 15 amp plugs.Even though the load exceeds 12A? My case load is 13A. I have another appliance load is 14A.
1800 watt hair dryers don't run for very long at a time either. If they did run fairly continuously they would likely have 20 amp plugs on them.The manufacturer of the equipment determines the size of the plug based on the listing. 1800 watt hair dryers have 15 amp plugs.
True, my point was that if it comes with a 15 amp plug then no one should be concerned if it's plugged into a 15 or a 20 amp circuit.1800 watt hair dryers don't run for very long at a time either. If they did run fairly continuously they would likely have 20 amp plugs on them.
Some kitchen appliances fit into similar situation.
There was one at one time rated 1875 watts, at 125 volts with a 15 amp plug.True, my point was that if it comes with a 15 amp plug then no one should be concerned if it's plugged into a 15 or a 20 amp circuit.