Does it exist?
Like this, but weatherproof.

They want a disconnect at the well site for the single phase well pump. They are usually about 8 amps, so I plan to use a 20 or 30 amp 2 pole toggle switch, but I'm running #10 wiring out there for VD, and using 1" PVC because I like to make life easy for myself. Maybe 3/4" if I'm feeling ambitious and I can't find a 2 gang box with 1" KOs.
Like this, but weatherproof.

They want a disconnect at the well site for the single phase well pump. They are usually about 8 amps, so I plan to use a 20 or 30 amp 2 pole toggle switch, but I'm running #10 wiring out there for VD, and using 1" PVC because I like to make life easy for myself. Maybe 3/4" if I'm feeling ambitious and I can't find a 2 gang box with 1" KOs.