Standby Generator Sizing 702.4 (b)(2)(a)
Josuea1990
Florida, USA
Greetings!
Whole house generator with ATS question:
So, it seems to me that in every YouTube video I've watched about standby generator installs with whole house automatic transfer switch on houses that have a 200 A service, and in other, even a farm with A 400 A service with two 200 A panels being fed by a 24 kw generator, they are all just not following 702.4 (b)(2)(a), and they even show that they passed inspection and even had utility come disconnect and all that jazz. I keep scratching my head on ¿how are they passing inspections? Since they all talk very loosely on how to size it. Never mention anything about load calculations in article 220 since the whole house is being automatic transfered, and they just speak about what appliances they would like to run during a power outage as if these appliances were all electric (because if they were not, then why would they be so worry to be able to run them with generator power) things like a/c, cooking, heating and lights and internet they loosely mention for houses that i can clearly see are douple or triple the sq.ft. of my Apt. which i used to compare. They are esentially sizing it based on personal preference.
For example: I live in a 1080 sq.ft. Apt. all electric, and I performed an optional load calc. to see what size Gen. would i be requiered, if I were to install whole house auto. transfer Well, result was 22kw (22kw÷240= 91.66 A) minimum and it makes sense because I have a 100 amp main. At one point somebody applied this same calc. on my dwelling unit in the past and decided to install 100 amp main. And on this videos I've watched they are picking arbitrarily numbers for all electric house (it seems), and clearly double or triple the sq.ft. of my home. For example, on the video with the farm guy he don't have natural gas, so he had propane installed for his 24 kw Gen. feeding two 200 A panels (meaning he never had gas, so he is all electric) and he passed inspection.They all pick 24, 22, 20,18, even 14 kw units.
Just the other day here in florida, even my boss told me on the phone (after I went rushing stretching my 100 ft tape measure around an all electric costumer's house to figure out the total 1968 sq.ft. and took pictures of all nameplates, then sit in the van to make an optional calc. and come up with a 28kw which we don't even carry, since the max we carry is 26kw, to give an estimate (all in 30 min). He says: "well, that 200 A house will do well with a 22 kw. And after the scared reaction for the 22kw price of the costumer who was expecting us to auto transfer the whole house, my boss asked me to say that we can do it cheaper and install an 18kw and they'll be fine (even my boss is picking arbitrarily numbers to make the sale, knowing the costumer wants permit to be pulled, inspection and all that jazz).
How can you explain this videos with inspections passed? Then I tought: "well, maybe they are using 220.87 to come up with a lower number, although they never mention that". But even if they were, how do you explain the Florida videos when even my self went ahead to make sure if we floridians have acces to the maximum demand data history over a one year period from the utility Co. like in some other states. So i called them and asked them for a one year period data on an excell format, so then i could use the max tool on excell to find the highest 15 min or 30 min (however often your utility captures) interval kwh meter registration to then in turn convert that in to kw. Well, at least here in florida that format is not available, all they have is kwh by the hour (hourly insterval registrations) for every day of every month and you have to find it yourself by logging into your account in their website on your energy usage dashboard and by manually looking day by day through the 12 months history for the highest kwh registration wich becomes the same as your highest kw demand per hour, this is insanely time consuming for when you are trying to use this method to calculate for a costumer that's interested on a whole house automatic transfer to come up with the lowest (cheaper) gen. size requiered by code per 702.4 (b)(2)(a) and using 220.87 to comply with the calculation part because the actual historical demand will always give you the lowest number and you could beat the competition and make the sale.
Now between you and me, we know an average 200 A house withouth an EV charger does not see more than 75 amps on a regular basis, and 75x240= 18kw, so in reality, yeah! 18 kw (don't worry about starting currents on A/C generac is rated to withstand them) will do the costumers house based on real history usage peak demand per 220.87, but if i can't get that paperwork from the utility, how can i prove it to the inspector?.
Now, what is going on with me? I'm I the only one worrying to comply with 702.4 (b)(2)(a) ? What if the inspector fail us for not sizing the generator properly, after purchasing materials and generator and start doing the job and all that jazz? Is it that inspectors don't really care because there is no safety hazard involved in it? I mean the worst thing that can happen is that the generator it self won't hold and trip it's own breaker right? or fail due to overloading or simply reduced its lifespan, which ultimately the only affected one will be the costumer, who'll end up with no power and a broken generator. Maybe that is why they are not requiring 702.4 (b)(2)(a) to be followed? What do you think ? I mean, at the end of the day is an "OPTIONAL" standby system.
No load shedding is being used in the videos I've watched.
What size generator would you pick for an all electric house that has a 200 A service and wants a whole house ATS without the use of load shedding? Would you pick an arbitriary number? Or would you follow 702.4 (b)(2)(a)
Thank you!
Do your load calcs like you have already done.
If it is over generator size, figure out a way to shed things one at a time until you are under the calc.
A/C and hot water are usually the easiest.
If you came out at 28k, and the generator you will propose is 26k, then shedding one of those will probably get you under calc.
That is why they sell so many larger gensets, the price difference is marginal but the load calc gets so much simpler.
Own house example: note: I did NOT bother to read the entire epistle of OP, just the last line ... ignore 704.....
Manual start not automatic. 6kW genset feeds main panel for heat pump water heater, well, and all other house loads. My wife is smart enough to not try to run clothes dryer and electric oven and a space heater at the same time <G> I'm actually bright enough to not try to use the welder during power outages :whistle:
2nd gen set feed 100A panel (which has dis-connect to main panel during outages) that feeds the GSHP (draws 15A inverter feed) and some outlets.
I did not read the entire post. Run on sentences, lack of punctuation, and lack of paragraphs, make for tedious reading.
First, YouTube is not an authority on anything. It’s a free platform where any JackWagon can upload anything and claim to be anyone. This is why it’s so scary that so many people are using YouTube in place of industry accepted textbooks to learn things.
Second, I install a lot of generators, and I have never been asked to provide a load Calc, either during plan check, or at final inspection. Load calcs are so incredibly conservative, and I think that plan checkers trust that at least most of us electricians here know how to size a generator.
Third, load shedding, as was mentioned. It can be done with modules, or sometimes you get lucky and something like the A/C, hot tub, and workshop are on the main panel, and we just backup the sub panel in the house.
I have a 26kW at the ranch. It runs 2 houses, and an auxiliary unit, and my shop. 2 laundry rooms with a total of 3 washers and 3 dryers, a 50A hot tub, commercial dish machine, commercial espresso machine, along with all the lighting and whatever life is going on.
I have not yet installed the module for the hot tub. 😚 But we lose power all the time, and the MCB on the generator has never tripped.
I’ve never installed anything bigger than a 22 on a single family residence. I’ve done 25 Liquid and 26 air cooled on sites with multiple homes.
I think 2023 was a big change for home generator installers.
If you look closely recent codes like the 2023 now require a article 750 Energy Management System (EMS) I dont think the 'load shed' in a common 200A ATS qualifies as a listed EMS or last I checked a Generac load shed was not a EMS but they offered a UL Listed EMS as a option for extra $$$.
Also an article 220 calc is required in more recent codes but in the past it was not explicitly required.
When I started, load calcs were not required for the permit. Then when the generator crazies hit, they were definitely required, and have been ever since. They also used to not require a gas calc, then they required gas plans in detail for the whole house, then they stopped caring after that.
Also depends which county. Some counties require the Optional Method even though it is not valid under 100 amps, which most generators are. Sssh. Don't tell them. It leads to a more manageable number anyway.
Yes. 702 b2a says you csn use whatever calculation method in article 220 l, and 220.87 is one them (this method uses the worst case scenario per say, based on your history usage) but unfortunately, here in florida they don't hande it to us as easy as in Austin for example where I have a friend that he got it there as a spreadsheet. Over his meter captures his power consumption every 15 min, he used the max function in excell and found the highest registration at one afternoon from 4 to 4:15 pm when he had family came over at a certain date over the past one year period, and the registration was 2.6 kwh. So then he convert that into kw by dividing 2.6 by .25 (since 15 min is .25 of an hour) and the result was 10.4. And there you 10.4 is his maximum power usage based on his historical max demand data per 220.87.
10,400 w divided by 240 V= 43.33 Amps and this many amps is the max registered over a year period. That means he could use a 10.4kw minimum generator to power his entire house when using an ATS and comply with 702.4 b2a
Can I ask why even do a load calc when you can get peak demand from powercompany???? There an allowance for that!
Not really accurate enough to size a generator, at least with the info I’ve been able to attain from power bills and such.
Best it’ll show is hour by hour usage. A place that has a lot of motors for example, especially ones that startup when power is restored, like a well pump that shut down due to low water, really needs to be gone over by the electrician on site.
I find the whole automatic part overblown for most residential. I had a customer who hated it it, said it ran out his propane tank, his neighbors complained about the noise at night etc. I don't think he realized how many loads he was powering (I did not install it).
He wanted to decide when to run it but wanted it 'on' for the exercise feature and to keep the battery charged. He has disabled the ATS by adding a toggle switch in the ATS to operate the ATS. When the power is out and he's home and he wants power he flips off all his breakers except two, he fires up the generator (with the toggle) for a few hours then back off.
Honestly, an ESS/battery storage with a dc generator that comes on to top off the batteries would be the ideal situation. Unfortunately it’s also expensive.
Generac was going to come out with a DC generator that was supposed to integrate with the PwrCell and inverter. Never came to market, not sure why.