milmat1
"It Can't Do That !"
- Location
- Siler City, NC USA
- Occupation
- Controls Engineer
Friends.
I have a 480 VAC brake-motor on a hoist. The Stearns brake has an inrush of 5 amps and holding current of 0.4 amp. Saturn hoist had fused the brakes with time delay 0.5 amp CC fuses. However, I want to use a breaker with aux contact so i can receive the status of the brake voltage in the PLC. [ During install they ran the motor without the brake fuses installed and fried the friction disc !]

I don't know where in the NEC to look for this type of protection. I am thinking of using a breaker with a deep curve (D") and rated at 1 amp. But not sure where to look to confirm this is OK ??
I have a 480 VAC brake-motor on a hoist. The Stearns brake has an inrush of 5 amps and holding current of 0.4 amp. Saturn hoist had fused the brakes with time delay 0.5 amp CC fuses. However, I want to use a breaker with aux contact so i can receive the status of the brake voltage in the PLC. [ During install they ran the motor without the brake fuses installed and fried the friction disc !]


I don't know where in the NEC to look for this type of protection. I am thinking of using a breaker with a deep curve (D") and rated at 1 amp. But not sure where to look to confirm this is OK ??