Air compressor opinion
dm9289
Industrial Maintenance Electrician
Pennsylvania
Industrial process repair/ maintenance Electrician
We have an air compressor @ 480 v the full package current is 293amps.
For wire and breaker sizing does this sound correct
293x1.25=366A
500kcm copper THHN @ 75degrees=380amps
400amp Circuit breaker
Equipment of this nature is generally specified with a minimum circuit ampacity (MCA) and a maximum overcurrent protection device (MOCP). Do you have access to that information?
Thank you for your reply but only the tag shown. I have been reaching out to the manufacture. I did find online they recommend 500kcm. It is a Y delta start. It does some form of cycling but never shuts off.
I would likely treat it like a motor and use a circuit breaker larger than 400A. Maybe as large as 600.
Buried amongst a bunch of stuff i did find and engineering data sheet. Max breaker 500 amp and thank you everyone!
Probably an air screw. Smaller ones do eventually shut down, if no air demand after a preset time. Timer resets, don’t know about the big ones.
This one never shuts off except when it goes boom.
I was going to say the 400 is probably not large enough. Something that size probably starts unloaded though and probably runs all the time loading and unloading or it could be a VFD
Wye Delta starts require some extra load calcs. These starters do not involve a drive. The concept is to start under wye config and then revert back to delta to run. The compressor is being ran using both winding configs. This helps reduce inrush current loads on startup
I have not dug deep yet but has the 2 sets of contacts
Well if from the starter to the compressor is 6 conductors for the Wye start Delta run configuration then the conductors are sized at 72% of the FLC. (58*125%) since the conductors will each carry 58% of the FLC.
The nameplate says it has a 200HP motor and an additional 7 HP of other loads.
It also shows a ridiculously low SCCR of 5kA.
That's why I initially though that the circuit feeding this would be terminating in a control panel. I guess we need more details to give an accurate answer.
There is at least a Y-D starter and some power distribution blocks. I don't know of any 200HP starter that is only 5kA rated, but I might be thinking of 47 years ago.