Use Of Materials
Branford Florida
Electrical Contractor
Electrical Contractor Here asking the question: Does the NECA not allow a 12/2 Romex conductor to be terminated on a 15-amp breaker? We pulled 12/2 as home runs in a residential home and our local inspector says we can't put that conductor on a 15-amp breaker. Says it must go on a 20-amp breaker because the wire is rated for 20 amps
They're quite wrong. As long as the wire is protected at or below it's rating, you're fine. (Want to put a 6g on a 20a breaker? Go for it.) You might have to remind them about up-sizing for voltage drop issues.
Inspector is in correct and is IMO pretty clueless to think that the conductor has to match the OCPD size.
Your original post mentions #12 as "home run".
Did #14 ever enter into the picture >?
Maybe I'm being nit picking but he pretty much implied it.
Upsizing a home run is commonly done and a reason for his using a 15A to feed it. If the entire circuit was 12, why wouldn't you just use a 20A? No, you don't have to, but kinda a waste of money and effort because if the rest of the circuit
-Hal
Yeah long ago we ran #6 aluminum on an overhead service to an outbuilding for a 15 amp circuit just for voltage drop. I forget exactly how far but at least 200 if not 300 feet
IMHO the entire circuit should be the same size wire, unless it is done for VD and splices made at the beginning and/or end for smaller wire to connect to the breaker etc. If changing a panel your not going to search the entire house to look for problems. Unless its a motor or HVAC load it gets the 15A for 14s, 20A for 12s and 30A for 10s Unless you find a smaller breaker on a circuit you keep it that way
If the inspector is insisting on a 20A breaker on #12 he is wrong
Someone changing the panel should check to see which conductors are on the existing breakers and mark them accordingly.
How many guys use little tags with strings on them to label the conductors as they take them off? I didn't one time because it was a small panel and pulled my hair out over why one breaker wouldn't hold. Turned out they ran the switch leg from the boiler switch at the top of the stairs into the panel and spliced it into the boiler feed. So, being unaware, (don't know why, I had to have taken it apart) I put the switch leg from neutral to a new breaker thinking it was another circuit. 😖
-Hal
-Hal
Yeah a good electrician would check the wire and the breaker size before ripping out the old panel which is why an oversized conductor should never be a problem. I would make sure that the conductor size matched the breaker if it didn't then I would mark the conductors with a wire marker and make a note of it. For a 40 circuit panel it's literally a few minutes extra work. I would also mark and note any 240 volt circuits and AFCI or GFCI circuits to ensure that the neutrals got connected correctly to the breaker.
I can see someone in a rush just ripping it all apart without checking but then you're just asking for trouble.