Old 1950's - 60's 120/240 High Leg No Main, Proper N-G Bond location???

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Meter feeds into a trough, there are 4 fused disconnects above the trough feeding subpanels located around the building.

Where does the N-G bond belong? In the trough? In one of the fused disconnects?
 
All of them, and also anything upstream

I was thinking all four. Right now I think there is one in the trough, and I know there is a ground rod and a bond at each of the 4 sub panels, but before I lift the ones at the subpanels, I want to make sure it's done right at the service
 
Where does the N-G bond belong? In the trough? In one of the fused disconnects?
In all of the service disconnects.
250.24 (C) Main Bonding Jumper.
For a grounded system, an unspliced main bonding jumper shall be used to connect the equipment grounding conductor(s) and the service-disconnect enclosure to the grounded conductor within the enclosure for each service disconnect in accordance with 250.28.
 
I think I see what they did here. N-G bond in the trough. Fused discos have no neutral or ground bar, neutral just passes through each disco, and everything is done in rigid
 
Not the case here, but what if there was no neutral going to the disco? Suppose it was just the 3 phase conductors? To be compliant would you have to run a neutral to that disco's enclosure and bond it?
What is not the case?

Yes a neutral (,grounded conductor) must be run to each service disconnect for a grounded system. Even if the neutral is not being used , you need for bonding and fault clearing. The code in theory could allow a different color in those cases and not call it a grounded conductor, like you can do for an SDS, not sure why they don't.
 
Then they are not listed as suitable for use as service equipment.
I better check before I plan farther. If I have to replace them I'm just going to use a small 3 phase breaker panel with spaces for six 3 phase breakers. I think I have a new one in one of my storage containers
 
I better check before I plan farther. If I have to replace them I'm just going to use a small 3 phase breaker panel with spaces for six 3 phase breakers. I think I have a new one in one of my storage containers
Note that depending on what code you are on, the panel board would need a main breaker as service disconnects are no longer allowed to be in the same enclosure.
 
Note that depending on what code you are on, the panel board would need a main breaker as service disconnects are no longer allowed to be in the same enclosure.
I just checked the fused discos and they are labeled as "suitable for service equipment" so I plan to keep them. there are two Square Ds and two FPEs. One of the Square Ds does have a neutral/ground bar. The other three discos look like there was never one installed or someone removed them
 
I just checked the fused discos and they are labeled as "suitable for service equipment" so I plan to keep them. there are two Square Ds and two FPEs. One of the Square Ds does have a neutral/ground bar. The other three discos look like there was never one installed or someone removed them
Yeah I wouldn't bother replacing them unless there was something wrong with them.
 