Fused discos have no neutral or ground bar, neutral just passes through each disco, and everything is done in rigid
Those two statements are not compatible ... part of the listing requirements of equipment that is listed for use as service equipment is that the equipment have a neutral bar and a factory supplied main bonding jumper.I just checked the fused discos and they are labeled as "suitable for service equipment"