Piping from 1.5" to 1" NEMA 50 amp outlet
Greg1707
Alexandria, VA
Business owner Electrical contractor
I have a job installing a 50 amp RV power outlet for a car charger. The plan is to run the 8-2 UF through the attic and down the side of the house to the RV outlet. The UF cable will be sleeved in a 1" PVC conduit directly into the top of the box.
https://www.homedepot.com/p/Midwest...orary-RV-Power-Outlet-U054PP-U054PP/331418048
The power box has pre drilled holes for a 1.5" conduit hub. How do I transition from 1" PVC to the power outlet that is set up for a 1.5" conduit?
The receptacle in the link needs a 4-wire cable. As Infinity stated #8 UF-B cable will need to be on a 40 amp breaker and charge rate will need to be set at 32 amps.
OP says RV power outlet for a car charger. RV 50 amp power outlet is a 14-50 and has 2 ungrounded conductors, a neutral and an EGC. Seems he needs 3 wire with ground cable, and if only using #8 UF would need protected with 40 amp OCPD.
Ok. OP here. I have a job to install an outlet for a TESLA mobile charger. The charger is rated at 32 amps. I plan to run #8 UF cable. What type of outdoor outlet should I use? The instruction say NEMA 14-50. Is this not correct/
That's fine, since there are no 40 amp receptacles a 50 amp is permitted. The OCPD cannot exceed 40 amps for #8 UF cable.
Just wanted to add.
The hole in the top is to mount a 4-bolt hub. It is not designed to directly accept a conduit connector. You need to purchase the correct size hub to match your raceway if you are going to enter from the top.
Yes, and the hubs are not univerally compitable. Very frustrating.
Well their listing & directions is for a 4-wire connection. So that would include connecting the neutral.
Tesla should put 6-50 plugs on the cords if they want them plugged in with no neutral.
Actually the customer has to buy adapters to be able to use the cord for level 2 charging. I believe it comes with a 5-15 adapter. For many years when people purchased their cars Tesla would recommend the 14-50 adapter and to have an electrician install a 14-50 receptacle if they wanted level 2 charging. I have had a few customers recently say that Tesla recommended they purchase a 6-50 adapter if they didn't already have a receptacle to connect to.