I'm trying to reconcile this section with the manufacturers instructions for an Allen Bradley Drive.  The manufacturer instructions say a drive for a 10HP 480V motor needs a 25 to 40 amp fuse.  The trouble is 430.130(A)(1) basically says to size the fuse per 430.52(C)(1)......which gives me a 14*1.75=24.5.  So I don't see how Allen Bradley can recommend a 40 amp fuse here. (If you have a look a the exception the input current of the drive is 18.4 so still no 40 amp fuse allowed per the NEC)
I can't imagine AB's recommended fuses are a code violation so I'm wondering if anyone has any insight into what I'm doing wrong.