Looks like i could use some clarification on this again.
According to nec 312.6, table 312.6 B(2) is to be used if a conductor enters or leaves tge enclosure through the wall opposiye its enclosure.
However the 2023 NEC Handbook in exhibit 312.1 shows a 4/0 neutral terminating to a neutral buss that does NOT enter or leave the enclosure through the wall opposite its enclosure.
In contradiction, the handbook does not use the appropriate table 312 6A to determine the proper amount of wire space ( 4 inches)
Instead the NEC handbook uses table 312.6B2 with a result of 7 inches?