Feeding old all in one from new
kgw
AZ
Electrical Contractor
Seeking input...AHJ is allowing what I suspect may be a NEC violation. Am removing existing 200 Amp overhead utility service to CSED ("all-in-one"?). Installing new 200 Amp CSED and overhead service, 22 kW generator, and 200 Amp ATS. Existing CSED to be fed from ATS. Existing CSED neutral appears to have integral bond; branch circuit grounding and neutral conductors are terminated on same ground bars.
I proposed installing new insulated neutral bar kits in existing all in one, connected to bonded neutral in new CSED. with all existing branch neutrals terminated on new insulated neutral bars (leaving grounding conductors on existing ground bars). In that scenario,
neutral in new all in one would be grounded, abd bond at existing all in one would be elimimated.
AHJ will accept leaving existing all in one as-is (neutral bonded), fed from new all in one.
Seems to me that would create a parallel neutral path between old & new all in one.
TIA for input.
I'd make the ATS my service disconnect and just buy a regular meter base, no need for another meter/main, Group the meter base outside, and ATS is now your service disconnect, move all grounding and bonding to it.
I would rip out and replace the old meter/main with a new main lug panel and supply it with a new 4-wire feeder.
Wish I could figure out how to post a pic.
CSED = Combination Service Entrance Device, aka all-in-one. My plan is for the existing CSED to remain but become a sub panel fed from new CSED via ATS. Hope to reuse existing CSED to simplify the project, avoid reworking existing circuits. The issue is whether it's ok to have the neutral bonded at both CSED's.
Welcome to the forum.
You said you are removing an existing CSED and installing a new CSED. You also say that an existing CSED is being fed from a new transfer switch. How many of them are there on this project? What is a CSED?
CSED = Combination Service Entrance Device. No one here calls them that, we call them meter/mains with or without distribution
What you are proposing would be a violation more than likely. The best solution is use a meter/main/ATS/distribution, like what Generac is offering.
Second best is meter - SE-Rated ATS - distribution/sub panel. The only N-G bonding that should take place would be in the ATS.
Another possible issue with your scenario is if the existing main with distribution is listed as Only For Use as Service Equipment, it’s technically a violation to reconfigure that as a sub panel.
I may be the only electrician that doesn't like to use a transfer switch as a service disconnect.
  • Like
Reactions: kgw