completeaudio
We are changing out services on multiunit residential buildings with meter stacks. There is a 600 Amp main and existing 2/0 GEC to an underground water pipe along with an old single ground rod. To bring the Grounding Electrode System up to code we are adding two ground rods (min 6’ apart) and we’re using a bonding jumper from the existing 2/0 GEC (listed UG split bolt) with 6awg to connect the two new rods. 250.66A specifically says you dont need larger than 6awg for the rods unless going to another electrode that would require a larger conductor. The handbook actually has an illustration on this method and seems straightforward but of course new inspector today is disagreeing. Does this seem compliant?