Hello all,
I have a Waste Water Treatment Plant that has an 800A 3 Phase 480V service, and they currently only have a 180 kW Generator backing up a 300A MCC. The are other circuits that are fed from a 800A Main Circuit Breaker. The plant wants whole plant backup. Does my generator size need be as big as the system amperage or only as big as the existing load calculations, and adding roughly 40% for future growth?
The calculations I ran on the plant came up to needing a 348.42 kW size generator, times by 40% = 487.79.
487.79 kW = 586.72 AMPS
Would a 500 kW generator be sufficient in this scenario?
I have a Waste Water Treatment Plant that has an 800A 3 Phase 480V service, and they currently only have a 180 kW Generator backing up a 300A MCC. The are other circuits that are fed from a 800A Main Circuit Breaker. The plant wants whole plant backup. Does my generator size need be as big as the system amperage or only as big as the existing load calculations, and adding roughly 40% for future growth?