I want to make sure I understand the 240.21(c) correctly, so I ask this question. Do all design below comply with 240.21 (C) ? This is not an industrial installation. The transformer primary fuses are 80E.



In my opinion, all the three design meet the table 450. 3 (A). Someone think, in design 1 the 3000A secondary conductors are not protected by any OCPD and in design 2 the 3000A switchboard bus is not protected by any OCPD. But I think design 1&2 meet 240.21(c) (2) since the 240.21(c) (2)(1) (b) doesn't require the secondary conductors must terminate in a single circuit breaker or set of fuses.
I think NEC should add the wording " The secondary conductors shall terminate in a single circuit breakers or set of fuses" to 24.21(C)(2) as similar wording as 240.21(C)(6)(2) if they require a separate OCPD for the 3000A secondary conductors in design 1 and the 3000A bus in design 2. Let me know your ideas!



In my opinion, all the three design meet the table 450. 3 (A). Someone think, in design 1 the 3000A secondary conductors are not protected by any OCPD and in design 2 the 3000A switchboard bus is not protected by any OCPD. But I think design 1&2 meet 240.21(c) (2) since the 240.21(c) (2)(1) (b) doesn't require the secondary conductors must terminate in a single circuit breaker or set of fuses.
I think NEC should add the wording " The secondary conductors shall terminate in a single circuit breakers or set of fuses" to 24.21(C)(2) as similar wording as 240.21(C)(6)(2) if they require a separate OCPD for the 3000A secondary conductors in design 1 and the 3000A bus in design 2. Let me know your ideas!